Group: DynoMotion Message: 6036 From: daveymahomh600e Date: 11/12/2012
Subject: Inductive Proximity Switches
Hi Tom,

My 2-axis setup uses a KFlop and SnapAmp system and will be run under KMotionCNC.

I will be using inductive proximity switches as limit switches and my plan is to use the 12V from the SnapAmp to power them. Is it best to route the signal through the KFlop or the SnapAmp? I was planning to use the 50pin cable into the SnapAmp, but thought I should check with you first.

Thank you,
David.
Group: DynoMotion Message: 6038 From: Tom Kerekes Date: 11/12/2012
Subject: Re: Inductive Proximity Switches
Hi David,

The best choice would be the 8 opto isolated inputs on SnapAmp.  But there is not 12V coming out of SnapAmp.  You will need to add an isolated 12V supply for that purpose.

Regards
TK


Group: DynoMotion Message: 6040 From: David Stevenson Date: 11/12/2012
Subject: Re: Inductive Proximity Switches

Hi Tom,
 
I am supplying 12V from the power supply to KFlop, which I believe simply passes through the board. Is that suitable to use and feed back to the SnapAmp?
 
Thanks,
David.
 
 
-----Original Message-----
From: DynoMotion@yahoogroups.com [mailto:DynoMotion@yahoogroups.com]On Behalf Of Tom Kerekes
Sent: Monday, November 12, 2012 12:21 PM
To: DynoMotion@yahoogroups.com
Subject: Re: [DynoMotion] Inductive Proximity Switches

 

Hi David,

The best choice would be the 8 opto isolated inputs on SnapAmp.  But there is not 12V coming out of SnapAmp.  You will need to add an isolated 12V supply for that purpose.

Regards
TK


Group: DynoMotion Message: 6041 From: Tom Kerekes Date: 11/12/2012
Subject: Re: Inductive Proximity Switches
Hi David,

A PC Power supply has +5V and +12V with a common ground.   As you stated KFLOP passes the +12V through the board to several of the KFLOP Connectors (but not SnapAmp connectors).  You could use that to power your sensors if you wish.  Your Limit Switch wiring would then not be electrically isolated from KFLOP's ground or the PC's ground.  If your system doesn't have a lot of noise this shouldn't be a problem.

Regards
TK

Group: DynoMotion Message: 6042 From: David Stevenson Date: 11/12/2012
Subject: Re: Inductive Proximity Switches

Hi Tom,
 
That's good to know.
 
Thank you,
David.
 
-----Original Message-----
From: DynoMotion@yahoogroups.com [mailto:DynoMotion@yahoogroups.com]On Behalf Of Tom Kerekes
Sent: Monday, November 12, 2012 2:22 PM
To: DynoMotion@yahoogroups.com
Subject: Re: [DynoMotion] Inductive Proximity Switches

 

Hi David,

A PC Power supply has +5V and +12V with a common ground.   As you stated KFLOP passes the +12V through the board to several of the KFLOP Connectors (but not SnapAmp connectors).  You could use that to power your sensors if you wish.  Your Limit Switch wiring would then not be electrically isolated from KFLOP's ground or the PC's ground.  If your system doesn't have a lot of noise this shouldn't be a problem.

Regards
TK